Frequency Response Initiative Generator Event Survey. NERC Resources Subcommittee North American Generator Forum December 8, 2016
|
|
- Jean Stevens
- 5 years ago
- Views:
Transcription
1 Frequency Response Initiative Generator Event Survey NERC Resources Subcommittee North American Generator Forum December 8, 2016
2 Why Primary Frequency Response Is Important Essential for Reliability of the Interconnections Cornerstone for system stability Line of defense to prevent Under Frequency Load Shedding(UFLS) Prevent equipment damage Essential for System Restoration Droop response is critical in restoration efforts Hydro units and gas turbines are some of the first units to be restarted Compliance with NERC Standards BAL-003-1, BAL-001 Mitigate future regulations related to generator frequency response performance To accurately predict system events (Transmission Models) 2
3 2012 Frequency Response Initiative Report Lazy L 3
4 NERC Outreach OEM and Engineering Firms 4
5 Generator Governor Frequency Response Advisory Advisory issued February 5, 2015 Initiated by NERC Resource Subcommittee Interconnections frequency response has declined Eastern Interconnection Lazy L profile 2010 and 2013 Generator Survey Data Generator Governor Frequency Response Advisory 5
6 Turbine OEM Reach Out to Customer Base 6
7 What has been learned Deadbands Exceed Many Deadbands Exceed 36 mhz Deadbands Vary Many exceed 36 mhz or 2.16 RPM Droops Settings Vary Majority Droops reported 5% 7
8 What has been learned Outer Loop Control Coordination with plant DCS is a requirement when operating in MW Set Point Coordinated Control. 8
9 Reliability Guideline: Primary Frequency Control Posted December 15,
10 Primary response GE perspective 1. Basic governor always present. Used for startup, synch, over speed protection and other functions in addition to droop 2. Unit level load control with primary frequency regulation bias. Default on new units starting ~ 2011, also default on many retrofits to larger units. May need to be disabled or coordinated with plant control. 3. Plant level load control. Plant plant coordination with A/E. Open loop vs closed loop, steam unit considerations, coordination with turbine load controller etc. Simple algorithms, low or no cost in plant design phase. Recommendations Recommend Plant level primary frequency response be a contractual requirement on new plant so not change order mid-commissioning Clearly defined requirements ( ex. ERCOT 5.78%) also define what constitutes plant rated load ( ISO, prevailing ambient, supplemental sources etc) Example, minimum of X % response in Y seconds for Z mhz change in frequency Requirements will trickle down to turbine supplier Plant level testing Must coordinate frequency injection between systems 3. Site specific, co-ordination required 2. Default on modern units since ~ Always present Clearly defined requirements upfront save time and resources
11 Outer Closed Loop Controls Any closed-loop load controls can squelch or negate governor droop response (PFR) Must add a PFR bias or simulation component Subject to tuning: Proportional Integrating Outside controls usually executed at a slower scan rate (1 second)
12 Illustration Frequency Hz Graphic from GE info bulletin PSIB
13 Missing Illustration Frequency Hz 450 MW 153 MW for little more than 1 second +/- Dead Band MW 153 MW for little more than 1 second 150 MW Graphic from GE info bulletin PSIB
14 Example Frequency Hz 6 MW 450 MW 153 MW 456 MW +/- Dead Band MW 153 MW 150 MW Graphic from GE info bulletin PSIB
15 Example Frequency Hz 0 MW 400 MW 150 MW 400 MW 150 MW 100 MW Graphic from GE info bulletin PSIB
16 Frequency Hz Conventional Steam Plant 6 MW 400 MW 406 MW +/- Dead Band MW 16 Graphic from GE info bulletin PSIB MW
17 The Capability Goal Reliability Guideline: Primary Frequency Control In order to provide Primary Frequency Control, it is recommended that all resources connected to an Interconnection be equipped with a working governor or equivalent frequency control device. The primary focus of the Guideline is prime mover governors. Other forms of resources providing frequency response should have similar response characteristics described herein for governor MW GE7FA Gas Mark VIe Turbine Frequency Algorithm added to Plant DCS 17
18 Next Step: Generator Survey Three Interconnections: Eastern, Western and Quebec conduct periodic generator surveys based on selected events over multiple years to measure generators individual performance. The surveys intention is to bring awareness to the industry and assist the industry in improving primary frequency response. The purpose of this data collection is not related to compliance. The NERC RS and NERC Staff will select at least two events a year spaced out in such a way to allow generator to address any issues discovered. Surveys will be sent within a timely manner of selected frequency excursions. Generator owners should complete and provide survey data for all BES generators online at the time of the event. 18
19 Additional Details NERC will provide an address and instructions for survey responses. Additional webinars with OEM and Engineering firms to provide resources to the industry. 19
20 Generator Survey Form 20
21 Generator Survey: Historian Data Entry 21
22 Generator Survey: Results 22
23 Assessing Performance: Simplistic Grading System For Generators with headroom (between Pmin and 2% of Pmax), Generators who provide response in the proper direction and sustained it for the lesser of the event duration or for 1 minute. Generators whose MW output remained unchanged, was in the wrong direction, or withdrew response. 23
24 24
Reliability Guideline: Generating Unit Operations During Complete Loss of Communications
Reliability Guideline: Generating Unit Operations During Complete Loss of Communications Preamble It is in the public interest for the North American Electric Reliability Corporation (NERC) to develop
More informationBAL Real Power Balancing Control Performance Standard Background Document
BAL-001-2 Real Power Balancing Control Performance Standard Background Document July 2013 3353 Peachtree Road NE Suite 600, North Tower Atlanta, GA 30326 404-446-2560 www.nerc.com Table of Contents Table
More informationBAL Real Power Balancing Control Performance Standard Background Document
BAL-001-2 Real Power Balancing Control Performance Standard Background Document February 2013 3353 Peachtree Road NE Suite 600, North Tower Atlanta, GA 30326 404-446-2560 www.nerc.com Table of Contents
More informationAttachment A to Primary Frequency Response Reference Document. Initial Primary Frequency Response Methodology for BAL-001-TRE-1
Attachment A to Primary Frequency Response Reference Document Initial Primary Frequency Response Methodology for BAL-001-TRE-1 Page 1 Primary Frequency Response Measurement and Rolling Average Calculation
More informationPrimary Frequency Response Ancillary Service Market Designs
Engineering Conferences International ECI Digital Archives Modeling, Simulation, And Optimization for the 21st Century Electric Power Grid Proceedings Fall 10-24-2012 Primary Frequency Response Ancillary
More informationNotes Generator Verification SDT Project
Notes Generator Verification SDT Project 2007-09 FERC Office 888 First Street, NE Washington, DC 20426 1. Administration a. The following were in attendance: Bob Snow, Cynthia Pointer, Lim Hansen, Keith
More informationFrequency Response and Standard background Overview of BAL-003-1
Industry Webinar BAL-003-1 Draft Frequency Response Standard and Supporting Process July 18, 2011 Agenda Frequency Response and Standard background Overview of BAL-003-1 What s changing Field Trial Frequency
More informationMISO Reliability Coordination expansion 6/1/2013
NERC Resources Subcommittee MISO BA Integration Update April 2013 MISO Reliability Coordination expansion 6/1/2013 # Acronym BA Name CWAY 215 MW NLR 245 MW WMU 95 MW SME 1,601 MW 1 CLEC CLECO 2 SME South
More informationNERC Reliability Standard PRC-024 Generator Frequency and Voltage Protective Relay Settings
NERC Reliability Standard PRC-024 024-1 Generator Frequency and Voltage Protective Relay Settings Rick Terrill Luminant Power Generation Compliance NERC Standards Drafting Team Member Reliability Standard
More informationof New York, Inc. Original Sheet No. 81 SCHEDULE 3 Black Start Capability
SCHEDULE 3 Black Start Capability This service allows the transmission system to be restored from a blackout condition by repowering steam powered generators at various locations in Con Edison. These units
More informationI. History of Time Error Correction and Reduced Reliance On Manual TEC Today
Time Error Correction and Reliability White Paper Recommendation of the Balancing Authority Reliability-based Controls 2.2 Standard Drafting Team to Retire BAL-004-0 Time Error Correction The Balancing
More informationPhase 2 of System Protection Coordination (Requirement revisions to PRC ) Hydro Québec TransÉnergie
Project 2007-06.2 Phase 2 of System Protection Coordination (Requirement revisions to PRC-001-1.1) Industry Webinar March 24, 2015 Standard Drafting Team Member Mark Peterson, Chair Michael Cruz Montes,
More informationDefinitions. Common Corridor:
Definitions Common Corridor: Contiguous right-of-way or two parallel right-of-ways with structure centerline separation less than the longest span length of the two transmission circuits at the point of
More informationProject Reliability-based Control
Project 2007-18 - Reliability-based Control EXCEL WORKBOOK INFORMATION February 03, 2010 The Excel workbooks use a calculation of the Balancing Authority ACE Limit as defined in the draft Standard BAL-007.
More informationHornsdale 2 Wind Farm. FCAS Capability Test Plan
Hornsdale 2 Wind Farm FCAS Capability Test Plan Prepared by Siemens Wind Power Pty Ltd 885 Mountain Highway Bayswater VIC 3153 tristan.raysonhill@siemens.com daniel.gallagher@siemens.com Revision History
More information10/13/2011 Planning Coordination Committee. Standards
Document name Category System Performance Regional Criterion ( ) Regional Reliability Standard (X) Regional Criterion ( ) Policy ( ) Guideline ( ) Report or other Document date 12/01/2011 Adopted/approved
More informationDATA SHEET. Synchronisers, FAS-113DG ANSI code 25
DATA SHEET Synchronisers, ANSI code 25 Synchronisation of generator to busbar Circuit breaker time compensation LED indication of status LED for activated control LED for synchronising signal 35 mm DIN
More informationGC0100/101/102 Code Administrator Consultation Responses. Rob Wilson. Grid Code Panel 8 th Feb 2018
GC0100/101/102 Code Administrator Consultation Responses Rob Wilson Grid Code Panel 8 th Feb 2018 GC0100 Respondent Original/ Alternative Support Implementation Summary of Points View of Proposer EDF Energy
More informationVAR Generator Operation for Maintaining Network Voltage Schedules
Standard Development Timeline This section is maintained by the drafting team during the development of the standard and will be removed when the standard becomes effective. Development Steps Completed
More informationImproved Synchronization System for Thermal Power Station
Improved Synchronization System for Thermal Power Station Lokeshkumar.C 1, Logeshkumar.E 2, Harikrishnan.M 3, Margaret 4, Dr.K.Sathiyasekar 5 UG Students, Department of EEE, S.A.Engineering College, Chennai,
More informationDynamic Performance Requirements for Phasor Meausrement Units
Dynamic Performance Requirements for Phasor Meausrement Units 2010 February NAPSI Meeting Dmitry Kosterev Transmission Planning Bonneville Power Administration dnkosterev@bpa.gov Slide 1 BPA Plans for
More informationThis section is maintained by the drafting team during the development of the standard and will be removed when the standard becomes effective.
PRC-026-1 Relay Performance During Stable Power Swings Standard Development Timeline This section is maintained by the drafting team during the development of the standard and will be removed when the
More informationInter-Area Oscillation Damping by PDCI Modulation from PMU Feedback
Inter-Area Oscillation Damping by PDCI Modulation from PMU Feedback BPA Presenters: Hamody Hindi, Gordon Matthews Sandia National Labs: David Schoenwald Montana Tech: Dan Trudnowski BPA: Jisun Kim (PM)
More informationOperating Committee Conference Call and Webinar Meeting Minutes
Operating Committee Conference Call and Webinar Meeting Minutes October 10, 2012 1:00 p.m. 3:00 p.m. (EDT) The Operating Committee (OC) met by conference call and webinar on October 10, 2012 at 1:00 p.m.
More informationA. Introduction 1. Title: Automatic Underfrequency Load Shedding Requirements
DRAFT 6 V4 Standard PRC-006- RFC-01 01/11/11 A. Introduction 1. Title: Automatic Underfrequency Load Shedding Requirements Deleted: Deleted: 10 Deleted: 20 9 2. Number: PRC 006 RFC 01. Purpose: To establish
More informationFCP Project Summary report
Evert Agneholm (DNV-GL), Erik Alexander Jansson (Statnett) v 1.0 11 May 2017 Document version Draft Ver 1.0 11-05-2017 List of contents 1. Introduction... 3 1.1. Background...3 1.2. Aim...3 2. Constraints...
More informationUnofficial Comment Form Project Establish and Communicate System Operating Limits (SOL and SOL Exceedance Definitions)
Unofficial Comment Form Project 2015-09 Establish and Communicate System Operating Limits (SOL and SOL Exceedance Definitions) Do not use this form for submitting comments. Use the electronic form to submit
More informationDragon. manual version 1.6
Dragon manual version 1.6 Contents DRAGON TOP PANEL... 2 DRAGON STARTUP... 2 DRAGON STARTUP SCREEN... 2 DRAGON INFO SCREEN... 3 DRAGON MAIN SCREEN... 3 TURNING ON A TRANSMITTER... 4 CHANGING MAIN SCREEN
More informationBATTERY ENERGY STORAGE SYSTEM REQUIREMENTS FOR CONTINGENCY FCAS REGISTRATION
BATTERY ENERGY STORAGE SYSTEM REQUIREMENTS FOR CONTINGENCY FCAS REGISTRATION PREPARED BY: AEMO Operations Department Systems Performance & Commercial VERSION: 1.0 EFFECTIVE DATE: 14 January 2019 STATUS:
More informationNOTICE. (Formulated under the cognizance of the CTA R4.8 DTV Interface Subcommittee.)
ANSI/CTA Standard DTV 1394 Interface Specification ANSI/CTA-775-C R-2013 (Formerly ANSI/CEA-775-C R-2013) September 2008 NOTICE Consumer Technology Association (CTA) Standards, Bulletins and other technical
More informationSTATE OF OHIO DEPARTMENT OF TRANSPORTATION SUPPLEMENTAL SPECIFICATION 872 LIGHT EMITTING DIODE TRAFFIC SIGNAL LAMP UNITS JULY 19, 2002
STATE OF OHIO DEPARTMENT OF TRANSPORTATION SUPPLEMENTAL SPECIFICATION 872 LIGHT EMITTING DIODE TRAFFIC SIGNAL LAMP UNITS JULY 19, 02 872.01 Description 872.02 Prequalification 872.03 Material Requirements
More informationPEP-I1 RF Feedback System Simulation
SLAC-PUB-10378 PEP-I1 RF Feedback System Simulation Richard Tighe SLAC A model containing the fundamental impedance of the PEP- = I1 cavity along with the longitudinal beam dynamics and feedback system
More informationEA63-7D. Generator Automatic Voltage Regulator Operation Manual. Self Excited Automatic Voltage Regulator
EA63-7D Generator Automatic Voltage Regulator Operation Manual Self Excited Automatic Voltage Regulator SP POWERWORLD LTD Willows, Waterside, Ryhall, Stamford, Lincs, PE9 4EY, UK Tel: +44 1780 756872 -
More informationUNISONIC TECHNOLOGIES CO., LTD
UNISONIC TECHNOLOGIES CO., LTD PROGRAMMABLE PRECISION REFERENCE. DESCRIPTION The UTC TL431 is a three-terminal adjustable regulator with a guaranteed thermal stability over applicable temperature ranges.
More informationKNX Dimmer RGBW - User Manual
KNX Dimmer RGBW - User Manual Item No.: LC-013-004 1. Product Description With the KNX Dimmer RGBW it is possible to control of RGBW, WW-CW LED or 4 independent channels with integrated KNX BCU. Simple
More informationSouth Australian Energy Transformation
South Australian Energy Transformation PSCR Supplementary Information Paper ElectraNet Corporate Headquarters 52-55 East Terrace, Adelaide, South Australia 5000 PO Box 7096, Hutt Street Post Office, Adelaide,
More informationWorking Document. Chapter 1. Subject matter and scope This Regulation establishes ecodesign requirements for simple set-top boxes.
Working Document on a possible Commission Regulation implementing Directive 2005/32/EC with regard to ecodesign requirements for simple set top boxes Chapter 1 Subject matter and scope This Regulation
More informationA Parametric Autoregressive Model for the Extraction of Electric Network Frequency Fluctuations in Audio Forensic Authentication
Proceedings of the 3 rd International Conference on Control, Dynamic Systems, and Robotics (CDSR 16) Ottawa, Canada May 9 10, 2016 Paper No. 110 DOI: 10.11159/cdsr16.110 A Parametric Autoregressive Model
More informationVIBRATION ANALYSIS AND BALANCE REPORT. Sample Facility
VIBRATION ANALYSIS AND BALANCE REPORT Sample Facility Main Gas Turbine Generator DATA COLLECTED: 3/6/14 2 of 11 Customer Contact Title Company Job Location March 11, 2014 Subject: Vibration Analysis And
More informationEVC300i. Generator Automatic Voltage Regulator Operation Manual
EVC300i Generator Automatic Voltage Regulator Operation Manual 1. INTRODUCTION The EVC300i Voltage Regulator is thyristor base to control the DC exciter field power of conventional 50 or 60 Hz brushless
More informationEVC600i. Generator Automatic Voltage Regulator Operation Manual
EVC600i Generator Automatic Voltage Regulator Operation Manual 1. INTRODUCTION The EVC600i Voltage Regulator is thyristor base to control the DC exciter field power of conventional 50 or 60 Hz brushless
More informationHYL-080D1750G358. Constant current LED driver DALI Dimmable. LED Driver. Product description. Benefits. Interfaces.
Linear / area dimming Constant current LED driver DALI Dimmable Product description Dimmable built-in constant current LED Driver Adjustable output current between 1,050 and 1,750mA via DIP switch Max.
More informationStandard IRO Reliability Coordination Responsibilities and Authorities
A. Introduction 1. Title: Reliability Coordination Responsibilities and Authorities 2. Number: IRO-001-3 3. Purpose: To establish the authority of Reliability Coordinators to direct other entities to prevent
More informationStandard Development Timeline
Standard Development Timeline This section is maintained by the drafting team during the development of the standard and will be removed when the standard is adopted by the NERC Board of Trustees (Board).
More informationSimulation of DFIG and FSIG wind farms in. MATLAB SimPowerSystems. Industrial Electrical Engineering and Automation.
CODEN:LUTEDX/(TEIE-7235)/1-007/(2009) Industrial Electrical Engineering and Automation Simulation of DFIG and FSIG wind farms in MATLAB SimPowerSystems Francesco Sulla Division of Industrial Electrical
More informationA Parametric Autoregressive Model for the Extraction of Electric Network Frequency Fluctuations in Audio Forensic Authentication
Journal of Energy and Power Engineering 10 (2016) 504-512 doi: 10.17265/1934-8975/2016.08.007 D DAVID PUBLISHING A Parametric Autoregressive Model for the Extraction of Electric Network Frequency Fluctuations
More informationForm C: Type Test Verification Report
Form C: Type Test Verification Report Type Approval and Manufacturer declaration of compliance with the requirements of G98. This form should be used when making a Type Test submission to the Energy Networks
More informationForm C: Type Test Verification Report
Form C: Type Test Verification Report Type Approval and Manufacturer declaration of compliance with the requirements of G98. This form should be used when making a Type Test submission to the Energy Networks
More informationReal Time Monitoring for SMART Grid Initiatives Synchronized Measurement & Analysis in Real Time SMART program by
Real Time Monitoring for SMART Grid Initiatives Synchronized Measurement & Analysis in Real Time SMART program by Bharat Bhargava Armando Salazar Southern California Edison Co. IEEE PES General Meeting
More informationRESPONSE OF CHANNEL 5 BROADCASTING LTD TO OFCOM S CONSULTATION ON PROPOSED PROGRAMMING OBLIGATIONS FOR NEW CHANNEL 3 AND CHANNEL 5 LICENCES
RESPONSE OF CHANNEL 5 BROADCASTING LTD TO OFCOM S CONSULTATION ON PROPOSED PROGRAMMING OBLIGATIONS FOR NEW CHANNEL 3 AND CHANNEL 5 LICENCES Channel 5 is proud to be a public service broadcaster and wishes
More informationSystem Troubleshooting for
Brought to You by Presented by Part 2 of 4 A1 Part 2 of 4 Video Problems No Match for the TERMINATOR When electronic security systems fail or malfunction, more often than not it s something small and relatively
More informationR&S ZVA-Zxx Millimeter-Wave Converters Specifications
ZVA-Zxx_dat-sw_en_5214.2033.22_umschlag.indd 1 Data Sheet 13.00 Test & Measurement R&S ZVA-Zxx Millimeter-Wave Converters Specifications 28.01.2013 15:08:06 CONTENTS General information... 3 Definitions...
More informationHYL-035D0850G103. Constant current LED driver DALI Dimmable. LED Driver. Product description. Benefits. Interfaces.
Constant current LED driver DALI Dimmable Product description Dimmable Independent constant current Adjustable output current between 350 and 1,050mA via DIP switch Max. output power 35 W Up to 88 % efficiency
More informationSMPTE STANDARD Gb/s Signal/Data Serial Interface. Proposed SMPTE Standard for Television SMPTE 424M Date: < > TP Rev 0
Proposed SMPTE Standard for Television Date: TP Rev 0 SMPTE 424M-2005 SMPTE Technology Committee N 26 on File Management and Networking Technology SMPTE STANDARD- --- 3 Gb/s Signal/Data Serial
More informationFREE TV AUSTRALIA OPERATIONAL PRACTICE OP- 59 Measurement and Management of Loudness in Soundtracks for Television Broadcasting
Page 1 of 10 1. SCOPE This Operational Practice is recommended by Free TV Australia and refers to the measurement of audio loudness as distinct from audio level. It sets out guidelines for measuring and
More informationMICROMASTER Encoder Module
MICROMASTER Encoder Module Operating Instructions Issue 01/02 User Documentation Foreword Issue 01/02 1 Foreword Qualified Personnel For the purpose of this Instruction Manual and product labels, a Qualified
More informationPower Supply Testing: 400 Hz Operation
Power Supply Testing: 400 Hz Operation White Paper by: Brian Rinehart Special Projects Technical Director Crystal Group Inc. 850 Kacena Road., Hiawatha, IA 800.378.1636 crystalrugged.com Contact: leslie.george@crystalrugged.com
More informationText with EEA relevance. Official Journal L 036, 05/02/2009 P
Commission Regulation (EC) No 107/2009 of 4 February 2009 implementing Directive 2005/32/EC of the European Parliament and of the Council with regard to ecodesign requirements for simple set-top boxes
More informationVARIABLE FREQUENCY CLOCKING HARDWARE
VARIABLE FREQUENCY CLOCKING HARDWARE Variable-Frequency Clocking Hardware Many complex digital systems have components clocked at different frequencies Reason 1: to reduce power dissipation The active
More informationOfficial Journal L 191, 23/07/2009 P
Commission Regulation (EC) No 642/2009 of 22 July 2009 implementing Directive 2005/32/EC of the European Parliament and of the Council with regard to ecodesign requirements for televisions Text with EEA
More informationBPA s Network Open Season
May 2009 Summary Welcome to the Twenty Second National Wind Coordinating Collaborative (NWCC) Transmission Update! Kevin Porter of Exeter Associates, Inc. led the April 21, 2009, Transmission Update conference
More informationStaff Report: CenturyLink Cable Franchise
Staff Report: CenturyLink Cable Franchise Presented to: City Council July 24, 2017 Prepared by: Marty Mulholland, Director of I.T. Services Department James Erb, Senior Assistant Attorney, Legal Contents
More informationR&S SMBV-Z1 Reference Frequency Converter Specifications
Test & Measurement Data Sheet 01.01 R&S SMBV-Z1 Reference Frequency Converter Specifications Version 01.01, July 2011 CONTENTS Definitions... 3 Introduction... 4 Specifications... 4 Input signal...4 Output
More informationenglish SGC inverter series hf transformer input voltage up to 800 V touch screen built-in data loggers
english SGC inverter series hf transformer input voltage up to 800 V touch screen built-in data loggers SGC inverters: the best choice advanced technology SGC inverters feature advanced design and superior
More informationCROCODILE AUSTRIA VIDEOSYSTEM
Project Reference: A3 Project Name: Videosystem ITS Corridor: CROCODILE Project Location: Western part of Austria 1. DESCRIPTION OF THE PROBLEM ADDRESSED BY THE PROJECT 1.1 Nature of the Site The Austrian
More informationMitigation of Cascading Outages and Prevention of Blackouts:System-Wide Corrective Control
10th Mediterranean Conference on Power Generation, Transmission, Distribution and Energy Conversion 6-9 November 2016 Belgrade, Serbia Mitigation of Cascading Outages and Prevention of Blackouts:System-Wide
More informationPart-Turn Electric Multi-Turn Electric
Optional 7 Handwheel Available NEMA 4 Enclosure Approvals MAR s Only (Canadian Standard Association) Enclosure NEMA 7 Enclosure Approvals MAR s Only (Canadian Standard Association) Class I, Divisions 1
More informationR&S ZN-Z154 Calibration Unit Specifications
ZN-Z154_dat-sw_en_3607-0481-22_v0101_cover.indd 1 Data Sheet 01.01 Test & Measurement R&S ZN-Z154 Calibration Unit Specifications 25.06.2014 10:27:09 CONTENTS Definitions... 3 Measurement range... 4 Effective
More informationOLED Lighting in Automotive Applications State of the Art and Future Demands. OLEDs World Summit 2017, San Francisco, Dr. Werner Thomas, AUDI AG
OLED Lighting in Automotive Applications State of the Art and Future Demands OLEDs World Summit 2017, San Francisco, Dr. Werner Thomas, AUDI AG 2 Agenda 1. Overview 1 st automotive series applications
More informationSummary of Meeting and Actions
Meeting Name Frequency Response Working Group Meeting No. 9 Date of Meeting Wednesday, 28 th April 2010 Time Venue 10:00am 3:00pm Conference Room B2-1, National Grid House, Warwick This note outlines the
More informationUNISONIC TECHNOLOGIES CO., LTD TL431
UNISONIC TECHNOLOGIES CO., LTD TL431 PROGRAMMABLE PRECISION REFERENCE DESCRIPTION The UTC TL431 is a three-terminal adjustable regulator with a guaranteed thermal stability over applicable temperature
More informationAgilent Technologies. N5106A PXB MIMO Receiver Tester. Error Messages. Agilent Technologies
Agilent Technologies N5106A PXB MIMO Receiver Tester Messages Agilent Technologies Notices Agilent Technologies, Inc. 2008 2009 No part of this manual may be reproduced in any form or by any means (including
More informationTransmitter Interface Program
Transmitter Interface Program Operational Manual Version 3.0.4 1 Overview The transmitter interface software allows you to adjust configuration settings of your Max solid state transmitters. The following
More informationProduct Manual (Revision U, 10/2007) Original Instructions. SPM-A Synchronizer. Installation and Operation Manual
Product Manual 82384 (Revision U, 10/2007) Original Instructions SPM-A Synchronizer Installation and Operation Manual General Precautions Read this entire manual and all other publications pertaining to
More informationCommissioning of Accelerators. Dr. Marc Munoz (with the help of R. Miyamoto, C. Plostinar and M. Eshraqi)
Commissioning of Accelerators Dr. Marc Munoz (with the help of R. Miyamoto, C. Plostinar and M. Eshraqi) www.europeanspallationsource.se 6 July, 2017 Contents General points Definition of Commissioning
More informationModBox-850nm-NRZ-series
The -850nm-NRZ series is a family of Reference Transmitters that generate excellent quality NRZ optical data streams up to 28 Gb/s, 44 Gb/s, 50 Gb/s at 850 nm. These transmitters produce very clean eye
More informationThis document is a reference document that shows the menus in the 5500sc, 9610sc and 9611sc analyzers. There are 3 top-level menus:
Controller menus 5500sc, 9610sc and 9611sc analyzers DOC273.53.80566 Introduction This document is a reference document that shows the menus in the 5500sc, 9610sc and 9611sc analyzers. There are 3 top-level
More informationThe above chart is used in ISO method to determine the alarm and trip limit for rotating machines equipped with rolling element bearings.
In vibration analysis (with accelerometers) of rotating machines with rolling element bearing, the process industries are interested to know the failure of the machine well in advance to plan the spare
More informationAutomatic Under-Frequency Load Shedding (AUFLS) Technical Report
Automatic Under-uency Load Shedding (AUFLS) Technical Report August 2010 System Operator 6/08/2010 Page 1 of 124 System Operator Report: Automatic Under-uency Load Shedding (AUFLS) Technical Report Page
More informationThis Service Bulletin may be distributed only to those groups indicated below with a check mark: End-use customers, owners and operators
Document Number: 601-00004-104 Title: MFD Configuration Save and Restore for Release 4.1.1 and 8.1.1 Revision: 01 Date: 09 March 2012 1. Planning Information 1.1 Distribution/Eligibility This Service Bulletin
More informationR&S ZN-Z103 Calibration Unit Specifications. Data Sheet V02.01
R&S ZN-Z103 Calibration Unit Specifications Data Sheet V02.01 CONTENTS Definitions... 3 Measurement range... 5 Effective system data... 5 General data... 6 Ordering information... 7 2 Rohde & Schwarz R&S
More informationUNISONIC TECHNOLOGIES CO., LTD TL431L
UNISONIC TECHNOLOGIES CO., LTD TL431L PROGRAMMABLE PRECISION REFERENCE DESCRIPTION The UTC TL431L is a three-terminal adjustable regulator with a guaranteed thermal stability over applicable temperature
More informationObjectives and Methodology for the Over-the-air Television Transition
January 2017 Spectrum Management and Telecommunications Objectives and Methodology for the Over-the-air Television Transition Aussi disponible en français DGGPN-002-017 Contents 1. Intent... 3 2. Background...
More informationAnalysis of the Televisions Implementing Measure Eco-Design Directive for Energy-related Products (ErP) formerly known as Energy-using Products (EuP)
s Eco-Design Directive for Energy-related Products (ErP) formerly known as Energy-using Products (EuP) Intertek 70 Codman Hill Road, Boxborough, MA 01719 icenter@intertek.com 800-WORLDLAB www.intertek.com
More informationThis document is meant purely as a documentation tool and the institutions do not assume any liability for its contents
2009R0642 EN 12.09.2013 001.001 1 This document is meant purely as a documentation tool and the institutions do not assume any liability for its contents B COMMISSION REGULATION (EC) No 642/2009 of 22
More informationSTEVAL-TDR007V1. 3 stage RF power amplifier demonstration board using: PD57002-E, PD57018-E, 2 x PD57060-E. Features. Description
3 stage RF power amplifier demonstration board using: PD57002-E, PD57018-E, 2 x PD57060-E Features N-channel enhancement-mode lateral MOSFETs Excellent thermal stability Frequency: 1030 MHz Supply voltage:
More informationOkta 600, Roots pump, 230/400 V, 50 Hz; 265/460 V, 60 Hz
Okta 600, Roots pump, 230/400 V, 50 Hz; 265/460 V, 60 Hz Okta 600, Roots pump, 230/400 V, 50 Hz; 265/460 V, 60 Hz Similar Image Dimensions Technical Data Ambient temperature 5-40 C Cooling method, standard
More informationDigital Economy Seven Programmer
Digital Economy Seven Programmer Model: TRTD7N White Installation & Operating Instructions 1. General Information These instructions should be read carefully and retained for further reference and maintenance.
More informationR&S FSW-K54 EMI Measurement Application Detecting and eliminating electromagnetic
R&S FSW-K54 EMI Measurement Application Detecting and eliminating electromagnetic interference Test & Measurement Product Brochure 01.00 R&S FSW-K54 EMI Measurement Application At a glance The R&S FSW-K54
More informationSPECIAL SPECIFICATION :1 Video (De) Mux with Data Channel
1993 Specifications CSJ 0924-06-223 SPECIAL SPECIFICATION 1160 8:1 Video (De) Mux with Data Channel 1. Description. This Item shall govern for furnishing and installing an 8 channel digital multiplexed
More informationC8000. sync interface. External sync auto format sensing : AES, Word Clock, Video Reference
features Standard sync module for a frame Internal sync @ 44.1 / 48 / 88.2 / 96kHz External sync auto format sensing : AES, Word Clock, Video Reference Video Reference : Black Burst (NTSC or PAL) Composite
More informationNRDC Follow-up Comments to the 12/15/08 CEC Hearing on TV Efficiency Standards
NATURAL RESOURCES DEFENSE COUNCIL NRDC Follow-up Comments to the 12/15/08 CEC Hearing on TV Efficiency Standards NRDC respectfully submits these written comments as a follow-up to our oral testimony http://www.energy.ca.gov/appliances/2008rulemaking/documents/2008-12-
More informationOrbital 694XA Series. Ka BAND EXTERNAL REFERENCE LNB with rear anchor posts. Wide range of Frequencies and Bandwidths LNB 1855R 1000 XA-WN60
Orbital 694XA Series Ka BAND EXTERNAL REFERENCE LNB with rear anchor posts Wide range of Frequencies and Bandwidths How to order an Orbital 694XA Series Ka Ext Ref LNB Frequencies (GHz): LO Input Output
More informationJul03 Rev C EC
Product Specification Coaxial BNC Solder Receptacle Connector 108-12079 10Jul03 Rev C EC 0990-0940-03 1. SCOPE 1.1. Content This specification covers the performance, tests and quality requirements for
More informationINTEGRATED CIRCUITS DATA SHEET. TDA4510 PAL decoder. Product specification File under Integrated Circuits, IC02
INTEGRATED CIRCUITS DATA SHEET File under Integrated Circuits, IC02 March 1986 GENERAL DESCRIPTION The is a colour decoder for the PAL standard, which is pin sequent compatible with multistandard decoder
More informationAltaLink Management Ltd.
Decision 21317-D01-2016 Central Alberta Underground Fibre Optic Build July 12, 2016 Alberta Utilities Commission Decision 21317-D01-2016 Central Alberta Underground Fibre Optic Build Proceeding 21317 Application
More informationSoftware Wizard Makes Configuring the 2301E Easier Configuration Wizard Now Included in 2301E Service Tool
Software Wizard Makes Configuring the 2301E Easier Configuration Wizard w Included in 2301E Service Tool The 2301E Configuration Wizard makes it easier to set up and use the 2301E Load Sharing Speed Control
More informationCommunication Theory and Engineering
Communication Theory and Engineering Master's Degree in Electronic Engineering Sapienza University of Rome A.A. 2018-2019 Practice work 14 Image signals Example 1 Calculate the aspect ratio for an image
More informationUnderstanding the Effects of Output Power Settings When Evaluating n Reference Designs
W H I T E P A P E R Understanding the Effects of Output Power Settings When Evaluating 802.11n Reference Designs David Cohen Senior Director of Marketing Quantenna Communications, Inc. September 2011 Contents
More informationMulti-Media Card (MMC) DLL Tuning
Application Report Multi-Media Card (MMC) DLL Tuning Shiou Mei Huang ABSTRACT This application report describes how to perform DLL tuning with Multi-Media Cards (MMCs) at 192 MHz (SDR14, HS2) on the OMAP5,
More information